Fascinating insight from Netwok Rail (https://www.networkrail.co.uk/running-the-railway/our-regions/southern/disruption-at-victoria-and-london-bridge/) into a shutdown in the Croydon area on Wednesday.

Quote
Disruption at Victoria and London Bridge:
how it happened and what we are doing about it

John Halsall, Managing Director, Southern region

On Wednesday night, the signalling system that controls the safe movement of trains through Croydon shut itself down to protect itself from an external power supply problem.

A power surge from our external provider put too many volts into our supply for around 20 seconds.

Our system is designed to fail-safe, so every signal – the traffic lights of the railway – went red and every train was brought to a stand.

The result was that for almost an hour we were unable to run services on the busiest section of the UK’s railway, causing disruption that lasted until Thursday morning.

[continues]


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: broadgage on December 20, 2019, 09:34:27
Was there any effect on electrical equipment outside of the railway ? Or was this another case of railway equipment being highly sensitive to minor electricity supply fluctuations that no one else noticed.

For signalling equipment of such importance, was no standby supply available? At the very least, I would expect a UPS with a battery run time of some minutes, and with a duplicated mains voltage supply into the UPS.


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: SandTEngineer on December 20, 2019, 10:11:48
Was there any effect on electrical equipment outside of the railway ? Or was this another case of railway equipment being highly sensitive to minor electricity supply fluctuations that no one else noticed.

For signalling equipment of such importance, was no standby supply available? At the very least, I would expect a UPS with a battery run time of some minutes, and with a duplicated mains voltage supply into the UPS.

If you read it again it says it was a power surge, not a loss of supply.  Electronic signalling equipment has strict set voltage limits and if these are exceeded the electronic equipment involved will self isolate to protect it from all being blown to pieces......   Normally things will reset after the supply restores to normal limits, but perhaps in this instance it didn't for some time due to other external factors.


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: onthecushions on December 20, 2019, 10:37:45

If the CB opens then there is certainly a loss of supply, however caused, hi-volts or lo-volts.

If there was uninteruptable power available to turn the signals red then there was the same power around to maintain the system.

I despair of electrical engineers.

OTC


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: SandTEngineer on December 20, 2019, 10:43:24

If the CB opens then there is certainly a loss of supply, however caused, hi-volts or lo-volts.

If there was uninteruptable power available to turn the signals red then there was the same power around to maintain the system.

I despair of electrical engineers.

OTC

Lineside signalling equipment is not usually supported by a UPS, but by a standby diesel generator.  We don't generally utilise Circuit Breakers but use hard wired fuses which are not susceptable to voltage/frequency flucuations, but only to excessive currents.

Does your despair also apply to Signal Engineers...... :P


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: SandTEngineer on December 20, 2019, 11:04:12
I don't do TWITTER but apparently an explanation of what happened has been posted by NR here which seems to be the same info a in the link posted by Grahame in the opening topic post: https://mobile.twitter.com/networkrailse/status/1207703163358392322?s=21


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: IndustryInsider on December 20, 2019, 11:08:26
Very impressive explanation and apology from NR there.


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: ellendune on December 20, 2019, 11:16:48
Very impressive explanation and apology from NR there.

For those who don't do twitter it includes a link to a longer explanation on their website  (https://www.networkrail.co.uk/running-the-railway/our-regions/southern/disruption-at-victoria-and-london-bridge/)


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: onthecushions on December 20, 2019, 12:13:14
[

Does your despair also apply to Signal Engineers...... :P


No. I think they/you are marvellous, making me and mine blissfully safe in rail travel. Many thanks.

A pity S&T types don't train highways designers.

Season's greetings,

OTC


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: broadgage on December 20, 2019, 13:51:53
Was there any effect on electrical equipment outside of the railway ? Or was this another case of railway equipment being highly sensitive to minor electricity supply fluctuations that no one else noticed.

For signalling equipment of such importance, was no standby supply available? At the very least, I would expect a UPS with a battery run time of some minutes, and with a duplicated mains voltage supply into the UPS.

If you read it again it says it was a power surge, not a loss of supply.  Electronic signalling equipment has strict set voltage limits and if these are exceeded the electronic equipment involved will self isolate to protect it from all being blown to pieces......   Normally things will reset after the supply restores to normal limits, but perhaps in this instance it didn't for some time due to other external factors.

I DID read it properly. A UPS protects not only against complete loss of power, but also against voltage out of tolerance as was reported to be the case.
If the mains supply is present but with an excessively high or low voltage, then a UPS will either correct this via a built in transformer, or will revert to battery power.


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: Surrey 455 on December 20, 2019, 22:31:02
I was sitting on a very delayed train at London Bridge that night which was cancelled and later re-instated (although about an hour later) after I had got off and gone to Waterloo instead :(. I was impressed with the scrolling information screens on that train, a Southern 377. This told me that all trains would be delayed or cancelled due to power supply failure in the East Croydon area. A few days earlier I was on another Southern 377 when approaching Epsom, the scrolling display mentioned that there were no SWR  trains between Epsom and Ewell West because of a landslip.
I have never seen this up to date information on any other train before. Is it keyed in manually or transmitted from a control centre?


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: stuving on December 20, 2019, 23:42:33
I was sitting on a very delayed train at London Bridge that night which was cancelled and later re-instated (although about an hour later) after I had got off and gone to Waterloo instead :(. I was impressed with the scrolling information screens on that train, a Southern 377. This told me that all trains would be delayed or cancelled due to power supply failure in the East Croydon area. A few days earlier I was on another Southern 377 when approaching Epsom, the scrolling display mentioned that there were no SWR  trains between Epsom and Ewell West because of a landslip.
I have never seen this up to date information on any other train before. Is it keyed in manually or transmitted from a control centre?

It will be sent by radio, but perhaps set up in advance and triggered.

Bombardier's in-house CIS makers BTROS offer a Real Time Passenger Information System (RTPIS), of which they say:

Quote
Unlike the current PIS Systems, where the on-train modems communicate directly with a single remote ground based system fitted with a dial-up modem, the RTPIS converted trains communicate via an intermediate secure hosted Transmission Router. This arrangement enables RTPIS uploads, RTPIS downloads, route database uploads and GPS tracking operations to be available concurrently from multiple ground based support locations, enabling quicker and easier updates to the PIS system.

However, from 2013 if not earlier, the OTMR (on-board train monitoring recorder) on 377s had developed a bit and might do that already: "The OTMR has ship to shore capability and a real time passenger information system. GPS is used to verify the train’s position so that relevant messages can be transmitted for the location. This is being applied system-wide." (Piers Connor for Modern Railways March 2013)

But if it's Bombardier standard kit, almost new 387s could have it too.


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: Electric train on December 21, 2019, 12:54:28
I don't know the specifics of this particular event, but I do know something about the power supplies on the ***Southern Region*** of NR

First the term power surge is used in the rail industry by folks in the operating department, a true power surge would fry a lot of equipment other than just the signalling. It was more likely to have been a short loss of power, just a few milliseconds is sufficient for the signalling system to go into a fail safe mode.  Basically, many of the modules used in signalling have "crowbar" protection, this device shorts out the supply into the module if it sees voltage transient's or an unstable supply and blows the fuse in the module; the signalling will fail safe but this will stop or restrict the movement of trains until a tech has attended site.

NR ***Southern Region*** takes its power from a number of DNO and TNO Grid sites a fault on their system of on NR's own internal 33kV distribution network can be sufficient to cause the above yet to any user they might have notice the light dip a bit.

There are UPS around the NR signalling supply system but these are not always installed, a complex set of sums used by commercial people of ten overrides the Engineers choice.


*** as an Western Region (BR) it uncomfortable working in the Southern Region  ;D ;D ;D


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: ellendune on December 21, 2019, 13:38:31
First the term power surge is used in the rail industry by folks in the operating department, a true power surge would fry a lot of equipment other than just the signalling. It was more likely to have been a short loss of power, just a few milliseconds is sufficient for the signalling system to go into a fail safe mode. 

Why would NR say it was an over-voltage fault lasting 20 seconds or more then?


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: onthecushions on December 21, 2019, 15:42:26

There are UPS around the NR signalling supply system but these are not always installed, a complex set of sums used by commercial people of ten overrides the Engineers choice.


I'm intrigued but not surprised to learn the actual age of the railway's commercial people.

Greetings!

OTC


Title: Re: Signalling shutdown - Croydon area - Wednesday night 18.12.19
Post by: Electric train on December 21, 2019, 19:26:38
First the term power surge is used in the rail industry by folks in the operating department, a true power surge would fry a lot of equipment other than just the signalling. It was more likely to have been a short loss of power, just a few milliseconds is sufficient for the signalling system to go into a fail safe mode. 

Why would NR say it was an over-voltage fault lasting 20 seconds or more then?

Typically the low voltage supplies derived form the 33kV will change over to a second or even third supply within 2 to 10 seconds, provided there was an actual supply failure, the change over equipment in the substations has a little hysteresis built. Also it can then take the signalling system can take many seconds to start to recover. 

The timings in the system are deliberate



This page is printed from the "Coffee Shop" forum at http://gwr.passenger.chat which is provided by a customer of Great Western Railway. Views expressed are those of the individual posters concerned. Visit www.gwr.com for the official Great Western Railway website. Please contact the administrators of this site if you feel that content provided contravenes our posting rules ( see http://railcustomer.info/1761 ). The forum is hosted by Well House Consultants - http://www.wellho.net