Train GraphicClick on the map to explore geographics
 
I need help
FAQ
Emergency
About .
Travel & transport from BBC stories as at 09:15 26 Apr 2024
- Rail Britannia?
Read about the forum [here].
Register [here] - it's free.
What do I gain from registering? [here]
 02/06/24 - Summer Timetable starts
17/08/24 - Bus to Imber
27/09/25 - 200 years of passenger trains

On this day
26th Apr (2016)
DOO strikes start on Southern (link)

Train RunningCancelled
22:03 London Paddington to Bristol Temple Meads
Delayed
08:34 Didcot Parkway to Banbury
PollsThere are no open or recent polls
Abbreviation pageAcronymns and abbreviations
Stn ComparatorStation Comparator
Rail newsNews Now - live rail news feed
Site Style 1 2 3 4
Next departures • Bristol Temple MeadsBath SpaChippenhamSwindonDidcot ParkwayReadingLondon PaddingtonMelksham
Exeter St DavidsTauntonWestburyTrowbridgeBristol ParkwayCardiff CentralOxfordCheltenham SpaBirmingham New Street
April 26, 2024, 09:24:43 *
Welcome, Guest. Please login or register.

Login with username, password and session length
Forgotten your username or password? - get a reminder
Most recently liked subjects
[135] access for all at Devon stations report
[133] Labour to nationalise railways within five years of coming to ...
[38] Bonaparte's at Bristol Temple Meads
[24] Lack of rolling stock due to attacks on shipping in the Red Se...
[16] Cornish delays
[15] Theft from Severn Valley Railway
 
News: A forum for passengers ... with input from rail professionals welcomed too
 
   Home   Help Search Calendar Login Register  
Pages: 1 2 3 [4]
  Print  
Author Topic: Hot weather warning 25th July 2019  (Read 10731 times)
Adrian
Transport Scholar
Sr. Member
******
Posts: 171


View Profile
« Reply #45 on: July 31, 2019, 20:09:54 »

Presumably the overhead wires are also heated a bit by resistance losses caused by the current flowing. This would be very variable according to amount of traffic, not a constant.

Regardless as to the details, it is well known that the wires expand in the heat, and means to compensate for this are readily available.
So what went wrong ? Was the temperature greater than the maximum planned for ? If so that sounds like a basic error in design or installation. The temperatures though reaching a new record were still only about 1 degree higher than those previously achieved. I would expect infrastructure to function correctly up to at least 5 degrees higher than the previous record.

Or were the multiple failures not due to simple expansion of the wires, but something else related to the heat.

A few more quick calculations.  Contact wire has cross-section of 120 mm2, copper has resistivity 1.7 x 10-8 so 1.4 mOhm per metre.
If a train is drawing 10000 kW at 25kV, that's a current of 400 A, which would cause heating of 23 W per metre.

Heat capacity will be about 400 J per K per m, so rate of heating would be roughly 1 degree every 20 seconds.

Of course, I've ignored the heat generated at the point the pantograph touches the contact wire.  I've no idea how to estimate that, though any heating effect must surely affect the pantograph more than the wire.  Do pantographs get hot?
Logged
stuving
Transport Scholar
Hero Member
******
Posts: 7170


View Profile
« Reply #46 on: August 01, 2019, 00:01:32 »

Some people are never satisfied ... but here is the official reckoning of the maximum current capacity of Series 1 OLE (Overhead Line Equipment, more often "OHLE") (some of this will flow in the catenary wire, but not a lot as it's smaller and less conductive):
 
Ambient temperature28o C
Solar gain 980 W/m2
Wind speed0.45 m/s (1 mph)
Current531 A
Resulting wire temperature56o C
Notes:   
  • That applies for a conductor wire at end-of-life wear - 25% gone (so presumably down to 90 mm2).
  • The limit is for continuous current, and for 10 minutes or less it can be raised by 15%.
  • Under those conditions the wire itself can cope with 964 A, reaching 80o C, if the run is short enough for expansion to be less than 1 m.
  • If the wind is just a little higher - 3 m/s (6.7 mph) - at 30o C ambient, the current limit becomes 964 A.

I don't think starting current is a big issue -  nothing like the headache it is for 1500 V DC (Direct Current) OLE, anyway (think of a big goods loco in the south of France on a hot day, for example).
Logged
Do you have something you would like to add to this thread, or would you like to raise a new question at the Coffee Shop? Please [register] (it is free) if you have not done so before, or login (at the top of this page) if you already have an account - we would love to read what you have to say!

You can find out more about how this forum works [here] - that will link you to a copy of the forum agreement that you can read before you join, and tell you very much more about how we operate. We are an independent forum, provided and run by customers of Great Western Railway, for customers of Great Western Railway and we welcome railway professionals as members too, in either a personal or official capacity. Views expressed in posts are not necessarily the views of the operators of the forum.

As well as posting messages onto existing threads, and starting new subjects, members can communicate with each other through personal messages if they wish. And once members have made a certain number of posts, they will automatically be admitted to the "frequent posters club", where subjects not-for-public-domain are discussed; anything from the occasional rant to meetups we may be having ...

 
Pages: 1 2 3 [4]
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.2 | SMF © 2006-2007, Simple Machines LLC Valid XHTML 1.0! Valid CSS!
This forum is provided by customers of Great Western Railway (formerly First Great Western), and the views expressed are those of the individual posters concerned. Visit www.gwr.com for the official Great Western Railway website. Please contact the administrators of this site if you feel that the content provided by one of our posters contravenes our posting rules (email link to report). Forum hosted by Well House Consultants

Jump to top of pageJump to Forum Home Page